Good Question! Soil (Sub-Grade) requirements for SOG¡¯s are often misunderstood and can lead to serious slab defects. Generally a SOG requires soil that could be described as reasonable. The K-Value (or Modulus of Sub-Grade Reaction) is in effect a measure of the Sub-Grades Stiffness and is used in the design of SOG¡¯s. For a SOG it is generally recommended that this should be a minimum of 0.035 N/ mm3, and this should ideally be proven with a Plate Bearing Test. The actual K-Value has a small influence on the required slab thickness.
However soil at deeper levels below the ground surface have the most significant effect on the long term settlement of the slab, therefore it is always recommended that the Client engage a Specialist Soils Engineer to review the soil conditions and if in doubt to estimate the anticipated long term or differential settlement. It is important to note that Soil Bearing Capacity (KN/ m2) is not a factor used in the design of modern SOG¡¯s – Bearing Capacity is used for the design of Foundations and Raft Slabs, not concrete pavements!
|